VAV system with constant air flow rate(EnergyPlus)

Hi! now i am running a VAV system with EnergyPlus.

i just found that the supply air is supplied in same flow rate constantly specially in summer.

but it is weird that air supply flow rate changes variably in winter and spring

what in this case, objects should i check for variable flow rates?

joooon's avatar
119
joooon
asked 2017-12-18 11:45:34 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-12-19 11:35:10 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Could you provide more information on your system such as air handler objects and terminal unit types, and any schedules related to your fan objects?

kramerica's avatar kramerica (2017-12-19 13:47:35 -0500) edit
add a comment see more comments

1 Answer

1

Check your air handler fan objects types and if Fan:VariableVolume its max and min values, terminal units, sizing:system field central heating maximum system airflow ratio, and sizing:zone field heating max airflow fraction.