100% unmet hours in chilled water system

I have an HVAC system consisting of 2 electric chillers in a college. For some reason, my reported unmet hours are 100% although the system is operating (chillers producing 100 kW cooling load).

I've put Setpoint Manager: Warmest on the demand side for Supply Air Temperature, and also set schedules for cooling thermostat of 20°C on the Thermal Zone tab. Checking the outputs I see some zones temperatures are rising as high as 30°C.

What can I be missing here?

Yael's avatar
249
Yael
asked 2017-12-11 13:09:26 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2017-12-12 03:23:13 -0500
edit flag offensive 0 remove flag close merge delete

Comments

1

@Yael Could you post a link to your model?

Avi's avatar Avi (2017-12-12 03:00:51 -0500) edit

You two chillers are perhaps just undersized. Try increasing the capacity ten folds, see if you still have the same problem.

Julien Marrec's avatar Julien Marrec (2017-12-12 03:24:05 -0500) edit

@Avi How can I post a link of my model? I have two chillers that are big enough,however not all their capacity is used (on all operation modes). I suspect it may have something to do with my part-load ratio characteristics: I'm using 2 chillers, each of them contains 2 circuits with 4 scroll compressors (2 compressors aligned on each circuit). I have 4 steps of capacity: 25%, 50%, 75% and 100%. The way I defined the ratios: minimum PLR 0.1, max PLR 1, optimum PLR 0.25, minimum unloading ratio 0.25. Can it be that not all the compressors are operated because I defined something incorrectly?

Yael's avatar Yael (2017-12-12 06:10:37 -0500) edit

@Yael you could upload it to some cloud service (Dropbox, google drive etc.) and share the link.

Avi's avatar Avi (2017-12-12 06:25:48 -0500) edit

Maybe start by exposing the plant output variables and examine how the plant loop performs

Avi's avatar Avi (2017-12-12 06:27:07 -0500) edit
add a comment see more comments

1 Answer

2

The problem was solved, first by changing the type of chilled beams from passive to active. In addition I put setpoint managers: single zone cooling to each zone and that solved the problem completely.