exterior convection for inclined wall

If I have inclined walls in my models, is EnergyPlus by default automatically calculate the exterior convection coefficient using the Emmel or Blocken method? Note: I'm not inputting anything for the SurfaceConvectionAlgorithm:Outside

Thanks

teguh511's avatar
31
teguh511
asked 2017-11-16 15:44:36 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-01-28 09:47:49 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

From the Engineering Reference, the following algorithms will account for surface tilt when calculating exterior convection coefficients:

These algorithms can be used by adding a SurfaceConvectionAlgorithm:Outside object to your input file. Without this object, EnergyPlus will use the DOE-2 algorithm by default.

Aaron Boranian's avatar
14.1k
Aaron Boranian
answered 2017-11-17 12:04:50 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks Aaron. furthermore, I think there's something missing in the engineering reference on page 47 that explaining the DOE-2 for exterior convection.

------"h is calculated using Equation or Equation ..."------

which equations?

Thank you

Best regards,

teguh511's avatar teguh511 (2017-11-17 19:25:11 -0500) edit

@teguh511 sorry to take so long to respond. It looks that way in both the raw PDF and online formats, but my guess is that it is referencing the $h_{c,glass}$ equation above and $h_{c}$ equation below that line of text you reference.

Aaron Boranian's avatar Aaron Boranian (2018-01-28 19:31:43 -0500) edit