drop in absolute humidity when using HVAC:Template:Zone:PTAC

Hi everyone! I am simulating an existing building with a cooling split unit, using HVAC:Template:Zone:PTAC with a SingleSpeedDX with no dehumidification unit added. However, when I look at the results, there is a huge drop in absolute humidity indoors compared to outdoors (about 10g/m3). Can anyone explain me why or how can I avoid that?

Thank you in advance!!

hullaballoo's avatar
63
hullaballoo
asked 2017-11-15 10:22:33 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-11-15 13:39:36 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

A DX cooling coil removes both sensible (temperature) and latent (moisture) energy from the air stream. Water cooling coils also have this same property. When using a cooling coil in your simulation roughly 25% of the energy transfer will be moisture. So the result will be that the indoors are dryer than outdoors.

rraustad's avatar
13.8k
rraustad
answered 2017-11-15 10:29:18 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you for your answer! Do you know if there is any way to simulate a cooling unit which removes only the sensible energy and not the latent?

hullaballoo's avatar hullaballoo (2017-11-18 12:02:51 -0500) edit

Well, I've never tried this but you could make the SHR = 1. You must ensure that the total capacity and air flow inputs result in a supply air condition that is on the psychrometric chart (i.e., outlet air RH < 100%).

Coil:Cooling:DX:SingleSpeed,
  1.0,                !- Gross Rated Sensible Heat Ratio
rraustad's avatar rraustad (2017-11-20 07:46:09 -0500) edit

Thank you now it works just fine!!

hullaballoo's avatar hullaballoo (2017-11-24 12:10:09 -0500) edit