Override Heat Pump Thermostat Control Logic

I'm trying to model different thermostat control logics for an AirLoopHVAC:UnitaryHeatPump:AirToAir:Multispeed with DX coils. I'm able to institute deadbands by changing component availabilities using EMS, but now I would like to control the speed, speed ratio, and cycling ratio. However, I do not see any EMS actuators for speed or the speed and cycling ratios in the EMS Application Guide. Any suggestions on how I can accomplish this? Thanks.

Matthew_Boyd's avatar
113
Matthew_Boyd
asked 2017-10-26 07:40:43 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-10-26 07:44:25 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

I don't see any EMS actuators for Multispeed coils. Only for single-speed DX coils. You would have to modify the source code or request these actuators be added via the UserVoice suggestion web site at https://energyplus.uservoice.com/foru....

rraustad's avatar
13.8k
rraustad
answered 2017-10-26 08:51:33 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you. I wasn't aware of the suggestion site.