I am using the EMS in EnergyPlus and customizing surface variables such as Dry Bulb Temperature, Wet Bulb Temperature and Wind Speed. I am imposing a Surface Dry Bulb Temperature that takes into account the convective and radiative heat exchanges between the external surface and the environment. If I run the simulation with EnergyPlus, though, the heat gain from the sun is taken into account as well, using the radiation data in the EPW file. How can I turn it off? I can easily regulate the convective heat exchange, customizing the convection coefficient on each surface, but what can I do with the radiative heat exchange? If I set to 0 the incoming radiation I eliminate this contribution, but I also eliminate the sun contribution in terms of light and that's not ideal.

carlobianchi89's avatar
159
carlobianchi89
asked 2017-10-20 20:01:06 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-10-21 07:43:01 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

For opaque surfaces, in the Material object for the outermost material layers, set Solar Absorptance to zero to eliminate solar gains from the outside surface heat balance. Likewise to eliminate external thermal radiant exchange (with sky and surroundings), set Thermal Absorptance to near zero.