EnergyPlus SQL Query Returns Incorrect Value

I'm looking at the results a bit closer at the results from an SQL query in EnergyPlus and I'm finding some issues. I'm able to access the HVAC Sizing Summary report properly, but the Sensible Heat Gain Summary report is a bit odd. The SQL query appears to mix up the values from the table.

For instance, the value from the SensibleHeatGainSummary report, Peak Cooling Sensible Heat Gain Components table, and Equipment Sensible Heat Removal column returns 720 W. The query using the Python bindings in OpenStudio looks like this:

sql_query = select Value from TabularDataWithStrings WHERE ReportName=\'SensibleHeatGainSummary\' and ReportForString=\'Entire Facility\' and TableName=\'Peak Cooling Sensible Heat Gain Components\' and ColumnName=\'Equipment Sensible Heat Removal\' and RowName=\'ZONE 0\';

 sql_file.execAndReturnFirstDouble(sql_query).get()

The HTML report shows that 720 W is the value for Lights Sensible Heat Addition. It is not the value for Equipment Sensible Heat Removal.

image description

Is there a mistake in my query syntax or a bug in EnergyPlus or OpenStudio? I'd greatly appreciate any help with this.

jmcneill's avatar
1.7k
jmcneill
asked 2015-01-29 11:33:26 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-11-07 14:22:19 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

4

I'm assuming you are using EnergyPlus 8.2.0. If you are then the problem is almost certainly a bug found in the original 8.2.0 release. The bug was patched in Update 1, available here. OpenStudio 1.6.0 is designed to work with this patched version of EnergyPlus.

Kyle Benne's avatar
6k
Kyle Benne
answered 2015-01-29 11:43:00 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks! I am using EnergyPlus 8.2.0. I'll let you know if that doesn't solve the problem.

jmcneill's avatar jmcneill (2015-01-29 12:14:46 -0500) edit
add a comment see more comments
3

This is related to SQL but not exactly related to your question, yet I don't think it needs a separate post as there is no answer to be given.

Anyway, the SQL issues still persist on 8.2.0 Update 1.

In EnergyPlus SQL output there are usually two main views, depending on what you asked in terms of output.

One is called TabularDataWithStrings and works as expected (contains all the tables from the report.html as far as I can tell).

The other one, is called ReportVariableWithTime and it is empty. The SELECT in the CREATE VIEW statement doesn't produce an error but doesn't return anything and that's the problem.

I've checked several sql files and the same problem is always present.

This was nonetheless fixed in the freshly out EnergyPlus 8.3.0 as far as I can tell, after running the same IDF file and checking the sql file.

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2015-04-02 10:03:01 -0500