heating load in energyplus

I'm new in HVAC system, and when I set an ideal HVAC system in energyplus, the output only shows the Zone Air System Sensible Cooling Rate, all the Sensible Heating Rate are zero, if I want to know the heating rate, what should I do ?

tianyang's avatar
73
tianyang
asked 2017-09-03 16:50:42 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-09-04 10:05:23 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

You will have to troubleshoot this a little more to find out what is happening. Try adding these report variables and plotting the results to understand the results.

Output:Variable,*,Zone Thermostat Air Temperature,hourly;
Output:Variable,*,Zone Thermostat Heating Setpoint Temperature,hourly;
Output:Variable,*,Zone Thermostat Cooling Setpoint Temperature,hourly;
Output:Variable,*,Zone Predicted Sensible Load to Heating Setpoint Heat Transfer Rate,hourly;
Output:Variable,*,Zone Predicted Sensible Load to Cooling Setpoint Heat Transfer Rate,hourly;

If you are simulating zone sizing then the eio file will show you the design heating loads. You will also need winter and summer SizingPeriod:DesignDay objects to complete zone sizing.

SimulationControl,
  Yes,                     !- Do Zone Sizing Calculation
  No,                      !- Do System Sizing Calculation
  No,                      !- Do Plant Sizing Calculation
  Yes,                     !- Run Simulation for Sizing Periods
  No;                      !- Run Simulation for Weather File Run Periods