PTAC with economizer in eQUEST?

I am trying to model single package vertical units (like this Bard product line) with economizers in eQUEST - I was thinking the eQUEST "Pkgd Terminal AC" would be a good system approximation for this equipment but then I don't believe I can include an economizer with that system type in eQUEST. Any suggestions on how to include an economizer on a PTAC in eQUEST or is there another workaround I could try?

pajordan's avatar
576
pajordan
asked 2017-08-16 15:16:33 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-08-16 15:38:35 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

I suggest using a PSZ in place of the PTAC. If you are concerned with part load performance, you can specify the PTAC curves for the PSZ system.

Chris Jones's avatar
1.1k
Chris Jones
answered 2017-08-17 09:23:05 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for the reply, Chris. With PSZ having to specify a return air path, would you agree Direct would be the best choice for a through-the-wall unit?

pajordan's avatar pajordan (2017-08-17 18:06:04 -0500) edit