1

Baseline Shading System

I'm modeling a Leed Baseline model.

The original building has a wide unconditioned roof. Should I consider it as a shading surface? Should I delete the unconditioned roof in the baseline model?

manfred's avatar
189
manfred
asked 2017-07-31 07:30:30 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2017-08-01 03:39:24 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Get a copy of the ASHRAE 90.1 vintage you are using in your LEED certification. Consider also getting the User's Manual that goes in pair with it.

ASHRAE 90.1-2010 (but same in 2007 and 2013 as far as I remember), Table G3.1, Section 5. Building Envelope, Baseline Building column:

f. Existing Buildings.

For existing building envelopes, the baseline building design shall reflect existing conditions prior to any revisions that are part of the scope of work being evaluated.

I would model it as per the baseline building, so included an unconditioned zone that will serve as your roof cavity, or whatever is actually the case.

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2017-08-01 03:42:53 -0500, updated 2017-08-01 03:43:50 -0500
edit flag offensive 0 remove flag delete link

Comments

I was looking for an explanation of this "existing conditions prior to any revisions that are part of the scope of work being evaluated.".

It's very clear, thank you very much.

manfred's avatar manfred (2017-08-01 04:17:15 -0500) edit
add a comment see more comments