LEED Baseline System 8, how many VAV?

I'm modeling a leed Baseline model with system 8.

My question is simple: how many air loops should I use? I've read (I don't remember where) I should use a single VAV for every floor, is it true? What if a have a huge building with just one floor?

manfred's avatar
189
manfred
asked 2017-07-29 10:10:39 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2017-07-30 03:11:44 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

LEED references ASHRAE 90.1, different vintages depending on the version/scheme of LEED you're using. I suggest you get a copy of the specific version you need, for example ASHRAE 90.1-2010 (LEED BD+C: Retail | v4 uses it)

But yes, that's one VAV per floor. Don't care if your building has 1 or 100 floors. In 90.1-2010 for example, if you have one floor but your area is still greater than 150,000 ft^2, and you have electric heat in the proposed, your baseline is a System type 8, and you'd only use one for the entire floor (except the exception areas...)

G3.1.1 Baseline HVAC System Type and Description.

HVAC systems in the baseline building design shall be based on usage, number of floors, conditioned floor area, and heating source as specified in Table G3.1.1A and shall conform with the system descriptions in Table G3.1.1B.

For systems 1, 2, 3, and 4, each thermal block shall be modeled with its own HVAC system. For systems 5, 6, 7, 8, 9, and 10 each floor shall be modeled with a separate HVAC system. Floors with identical thermal blocks can be grouped for modeling purposes.

Exceptions: [...]

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2017-07-30 03:10:36 -0500, updated 2017-07-30 03:11:33 -0500
edit flag offensive 0 remove flag delete link

Comments

I just was scared I missed some exceptions similar to table TABLE G3.1.3.7 (that set a chiller power limit).

Thank you!