4

openstudio Cooling Thermostat assign

Is there a faster way to assign cooling and heating thermostat schedules to a thermal zone? I am using OS thermal zone section and draging one by one from My model section. Same with zone equipment.

obuchely's avatar
1.4k
obuchely
asked 2015-01-21 15:21:26 -0500
Neal Kruis's avatar
4.7k
Neal Kruis
updated 2015-01-22 14:06:20 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

It is easiest to create thermostats that have your desired heating and cooling schedules and then assign the thermostats to zones while in SketchUp: image description image description

If most all of your zones have the same thermostat you can also use the "Set Thermostat Schedules" script (best to use in OS by using the apply measure now function). This script will assign all zones to a single thermostat, and then you can go change any zones that you want a different thermostat in.

Script is located here: Set Thermostat Schedules

Also, you can edit the script to assign a thermostat to only zones of a certain space type for example.

TaylorRoberts's avatar
2.9k
TaylorRoberts
answered 2015-01-21 15:51:59 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks Taylor. You save me lots of time. Is there a similar script to assign PTHP equipment to Thermal zones?

obuchely's avatar obuchely (2015-01-22 13:38:24 -0500) edit