Heating COP and Cooling COP

Dears

I use EnergyPlus for modeling a rectangular box, I need to identify the the values for Cooling COP using Chiller systems and Heating COP for Chiller system or Split AC units for heating. Also, provide me with reference for this values.

Regards ..

Hossam Wefki's avatar
53
Hossam Wefki
asked 2017-06-28 10:42:04 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-06-28 11:40:40 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

2

I don't know if you want to use it for project specific, or just for your own research. If your own research, you can use ASHRAE 90.1- standards. You can also connect with the manufacturers to provide you the cut-sheets if you are interested in a specific system.

Harshul Singhal's avatar
565
Harshul Singhal
answered 2017-06-28 11:38:35 -0500
edit flag offensive 0 remove flag delete link

Comments

For my research, I am an civil engineer, I don't have any experience in Mechanical systems. Now I perform simulation for energy consumption and i need to identify the values for COP for both heating and cooling.

Hossam Wefki's avatar Hossam Wefki (2017-06-28 14:07:24 -0500) edit
add a comment see more comments
1

Is this for an existing building or a new building?

ASHRAE Standard 90.1-2013 stipulates minimum equipment efficiencies for many types of HVAC equipment, listed in Table 6.8.1. If you don't have a copy of the standard, you can see the tables here on the FEMP website.

mdahlhausen's avatar
9.5k
mdahlhausen
answered 2017-06-28 11:41:32 -0500