why the wet bulb temperature of air is constant during the evaporative cooling?

why the wet bulb temperature of air is constant during the evaporative cooling?

amirrezaheydari's avatar
673
amirrezaheydari
asked 2017-06-07 08:32:36 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-06-07 08:38:24 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The definition of the thermodynamic wetbulb is the temperature of adiabatic saturation. i.e. it is the outlet temperature of air sent through a 100% effective adiabatic cooler.

Evaporative coolers can be modeled as adiabatic coolers with a prescribed effectiveness. With minimal piping and pump heat gain, the recirculating fluid can only exchange heat with the air stream. Without a heat source/sink, the fluid will quickly come to equilibrium with the inlet air, and no net heat transfer occurs. If the inlet air is not saturated, there will be sensible and latent heat transfer, but two will always cancel each other out. By the definition of the thermodynamic wetbulb, you should expect the wetbulb to be nearly constant in any evaporative cooling model.