HVAC Load Profiles is different to the sum of Zone Air System Sensible Cooling Rate

I´m learning Openstudio step and step, finally I reach the simulation results about "HVAC loads", unfortunately a question appeared, and I wondered if someone could solve.

The Sum of monthly HVAC load profiles is different to the sum of zone Zone Air System Sensible Cooling Rate. I thought it would be the same.

I´m using a Cooling district in order to discover the cooling demand. Maybe the different is the latent load, if it is true, which value should I reach, because I have used "Zone Total Internal Latent Gain Rate" and all values are 0.

gonchotorena's avatar
181
gonchotorena
asked 2017-05-29 17:09:28 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2017-05-30 02:37:01 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The difference is because you're not using the right reporting variable[1]. But yes, simply put the biggest difference is likely the latent load (but it could also be zone multipliers, etc).

You can get the total cooling rate from the HVAC system rather than the zone. What's the HVAC system you're using?

For example, if your district cooling serves terminal equipment that includes a Coil:Cooling:Water, you would use the Cooling Coil Total Cooling Rate (W).

If you use a ZoneHVAC:IdealLoadsAirSystem system, you would likely use Zone Ideal Loads Supply Air Total Cooling Rate [W].


[1] I also suggest you read in detail the section that explains what the Zone Air System Sensible Heating/Cooling Energy/Rate actually reports. It'll help you understand why this is not the variable to use if you want to sum them to match the DistrictCooling's cooling rate.

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2017-05-30 02:57:05 -0500, updated 2017-05-30 02:59:42 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for the answer, for years I have been used DesignBuilder and now I´m with Openstudio, and the name of the variables are quite more complex.

I´m going to read the links,

I set ideal loads, in order to set the heating demand and cooling demand.

Thanks.