OpenStudio: Ideal Air Loads

OpenStudio: Ideal Air Loads were turned on for a thermal zone that has no HVAC system, what does this mean? I found that overall cooling and fan electricity consumption decreased.

mcdonaa1's avatar
564
mcdonaa1
asked 2017-04-30 23:37:16 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

Ideal Air Loads will report the total district heating and cooling load that building experiences. It's not an actual HVAC system, so it won't have any fan electricity. Please refer to the input/output reference for more information.

Jonny K's avatar
554
Jonny K
answered 2017-05-01 00:32:23 -0500, updated 2017-05-02 16:32:50 -0500
edit flag offensive 0 remove flag delete link

Comments

1

The ideal loads are reported as "district" loads if I recall correctly.

ljbrackney's avatar ljbrackney (2017-05-01 10:45:57 -0500) edit

Good catch. I edited my answer above.

Jonny K's avatar Jonny K (2017-05-02 16:33:25 -0500) edit

district heating also includes water heating?

meiwen.zhou@wur.nl's avatar meiwen.zhou@wur.nl (2018-03-26 09:05:37 -0500) edit