I would like to switch on my cooling and heating systems when the operative temperature is out of the range of comfortable temperatures (i.g from 20°C to 28°C). Is it possible to set the setpoint temperatures so that the heating will be required when the zone temperature is lower than 20°C and the cooling will be required when the zone temperature is higher than 28°C ?

Jéssicamarasantos's avatar
91
Jéssicamarasantos
asked 2017-04-17 22:43:06 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-04-18 07:33:09 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

In the Activity tab set the Heating setpoint at 20C and the Cooling setpoint at 28C. Then enter in the Simulation tab, Options and select Operative temperature control. image description