2

The cooling load of result report is 0 in openstudio

I made a simple model with the ideal air load system, I only want to see the room load in the natural situation. But the cooling load from the output report is 0. Can anyone give me some tips? I have set Cooling Thermostat Schedule

Done's avatar
169
Done
asked 2017-04-09 07:57:19 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-04-13 13:48:09 -0500
edit flag offensive 0 remove flag close merge delete

Comments

You need to add more detail to this question in order for people to be able to give you meaningful answers. I also don't believe people are going to contact you via that email address.

Adam Hilton's avatar Adam Hilton (2017-04-10 07:46:36 -0500) edit
add a comment see more comments

1 Answer

4

Make sure you define BOTH a Heating Thermostat Schedule AND a Cooling Thermostat Schedule, even if you have no heating (put the heating tstat schedule to 0°C or whatever). If you don't do that, the thermostat:dualsetpoint isn't created when the model is forward translated and you end up with no cooling and no heating.

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2017-04-10 16:22:57 -0500
edit flag offensive 0 remove flag delete link

Comments

thank you! I can get the cool load while I set the Heating Thermostat Schedule.

Done's avatar Done (2017-04-10 21:26:56 -0500) edit

I'd appreciate it if you could upvote the answer if you found it helpful, and more importantly mark it as accepted since it solved your problem so that we can flag the thread as closed (please read the Help Page). Thanks.

Julien Marrec's avatar Julien Marrec (2017-04-11 05:46:02 -0500) edit
add a comment see more comments