Cooling Tower is storing excess heat the majority of the time

I have problem for modeling in water side.
Chiller COP is lower than 1 for all the time. Investigating the result, seems that condenser outlet and inlet temperature from chiller is so high (Inlet:53degC - 75degC, Outlet:58degC - 80degC) as shown in histogram below.
Then looking at the err file, found that Plant Loop: SD1 CW LOOP Demand Side is storing excess heat the majority of the time. Plant Loop: SD1 CW LOOP Supply Side is storing excess heat the majority of the time.enter code here
Does anyone know what is causing this warning and how I can fix this problem?

image description

katsuya.obara's avatar
2.1k
katsuya.obara
asked 2017-03-20 20:22:23 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Did you figure out the issue?

rkbest's avatar rkbest (2018-05-01 14:32:34 -0500) edit

Is the issue resolved ?

Siv's avatar Siv (2018-09-26 23:02:26 -0500) edit
add a comment see more comments

1 Answer

0

I've had the same problem with my heating loop. I Set the PlantLoop: Plant Loop Demand Calculation Scheme temperature setpoint to my loop design temperature and it get solve. I mean I'd set this setpoint at 60 deg and my boiler had been set on 82 deg. so I changed PlantLoop: Plant Loop Demand Calculation Scheme setpoint to 82 deg and it get solve.

taher.ahel's avatar
436
taher.ahel
answered 2018-08-23 14:38:12 -0500
edit flag offensive 0 remove flag delete link