heating and cooling energy consumption

Hi,

I have setting an energy model with Open Studio. I have not consider HVAC system, so I have only ideal air load. I would like to know electric consumption for heating and cooling.

after the simulation, within "results summary" label, there are some table about energy consumption for lighting and equipment but nothing for heating and cooling. Why? How do I set the ideal HVAC

Antop's avatar
353
Antop
asked 2015-01-10 12:59:52 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-07-12 18:12:40 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Ideal air loads doesn't know what fuel you are going to use for heating and cooling. For consumption look at district heating and cooling tables at the bottom of the results.

David Goldwasser's avatar
20.4k
David Goldwasser
answered 2015-01-10 15:38:59 -0500
edit flag offensive 0 remove flag delete link

Comments

hi, thanks for the answer I have seen the tables. I have energy consumption in district cooling, but nothing in district heating.

Which settings do I have to check ? Where do I have to set the fuel ? Can I change the units?

Antop's avatar Antop (2015-01-12 02:18:03 -0500) edit

Ideal loads does not have a selection for fuel type; it always uses district heating/cooling. If there is no heating consumption, then the first place to check is the thermostat heating setpoint schedule.

MJWitte's avatar MJWitte (2015-01-16 17:40:16 -0500) edit