air-to-air HVAC loop

I have created the following airloop, but I get this error: * Severe * IP: IDF line~4297 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 1, Required Field=[Zone 1 Name] was blank. How and where can I fix that? I have checked some other posts about this issue, and things like design days and design specification outdoor air seems to be fine.

image description

sga's avatar
123
sga
asked 2017-02-24 06:55:52 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Adam Hilton's avatar Adam Hilton (2017-02-24 08:27:05 -0500) edit

You also don't have any terminal equipment. You need something to connect the splitter to the zones.

Adam Hilton's avatar Adam Hilton (2017-02-24 08:28:15 -0500) edit

I have checked the question and I do not think any of the 5 errors mentioned occur in my file... How can I connect the splitter to the zones?

sga's avatar sga (2017-02-26 13:57:18 -0500) edit

Add an air terminal prior to the zone.

Adam Hilton's avatar Adam Hilton (2017-02-26 15:00:47 -0500) edit

I have added air terminal now, and the the analysis runs. However, I do not think it has any result on the temperature/humidity. Will this HVAC system warm up the incoming air by using the exhaust air (at least to some extend) and how do I set for example the temperature ranges I want to have? Lets say I want the temperature inside to be between 18 and 22 degrees. Thank you