Two chilled water loop with different temperature

Hi, I have a building that has 2 chilled water loop with different loop temperature. Each is cooled by a water-to-water heat pump and providing chilled water to different equipment. Is it possible to have 2 separate chilled water loop with water-to-water heat pumps rejecting heat to the same hot water loop in EnergyPlus?

Fish Lee's avatar
183
Fish Lee
asked 2017-02-20 01:46:25 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Yes, you can have supply equipment on different loops share the same condenser loop as demand equipment.

Adam Hilton's avatar
3.5k
Adam Hilton
answered 2017-02-20 08:02:24 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks. As my heat pumps are connected to the same condenser loop and hot water loop but to different chilled water loops, is it still possible to set up 2 central heat pump system and connect them as designed?

Fish Lee's avatar Fish Lee (2017-02-23 20:17:21 -0500) edit

Build the two chilled water loops and then put two heat exchangers on the demand side of those those loops that are supply components to your condenser water loop.

Adam Hilton's avatar Adam Hilton (2017-02-24 08:25:27 -0500) edit