E+ Tariff Measure Impacting Modeled Peak Electric Demand

I am attempting to evaluate several measures using the Parametric Analysis Tool. While setting up PAT I started by adding the "Tariff Selection Time and Date Dependent with Off Peak Demand Charge" to PAT only and comparing the results to the baseline. Stated differently, the tariff measure is the only measure I have added to my PAT file.

After simulating, the results show a 10% decrease in peak electric demand. I do not believe the tariff measure should impact energy use or demand, only the cost of energy. I've tried multiple configurations and each results in the 10% demand reduction. Any guidance would be greatly appreciated!

It appears that since I am new to Unmet Hours that I do not have enough points to upload files. If there is another way for me to share screenshots or files please let me know.

Phil Keuhn's avatar
41
Phil Keuhn
asked 2017-01-18 14:50:57 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-08-20 15:01:05 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

2

The only impact the tariff measure should have on non-cost simulation results is due to the timestep being changed to match a multiple of the tariff demand window length. Which specific measure are you using, and are you getting any info messages about the timestep changing?

David Goldwasser's avatar
20.4k
David Goldwasser
answered 2017-01-18 15:49:10 -0500
edit flag offensive 0 remove flag delete link

Comments

David,

Thanks for your help! I spent a day trying to figure that out. I aligned the time steps and the discrepancy in PAT went away. To answer your question the specific measure I'm using is named "Tariff Selection Time and Date Dependent with Off Peak Demand Charge".

Thanks again, Phil

Phil Keuhn's avatar Phil Keuhn (2017-01-18 17:23:06 -0500) edit
add a comment see more comments
1

Old question, but I'd like to point out that there can be two peak demand profiles when the model has a tariff with time of use demand charges; (1) the builing's peak demand profile and (2) the utility's peak demand profile, which may or may not be coincident. See the chart below for an example comparing the "Facility" demand from the Electricity:Facility meter and the "Utility" demand from the Tariff Report in EnergyPlus.

image description

MatthewSteen's avatar
10.1k
MatthewSteen
answered 2020-08-08 15:05:22 -0500, updated 2020-08-08 15:05:47 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments