possible incorrect IDD file

My model runs with HVAC comprised of VAV and reheat. However, if I switch to Ideal Air I get the following error:

Program Version,EnergyPlus-Windows-64 8.1.0.009, YMD=2014.12.30 01:21,IDD_Version 8.1.0.009
   ** Severe  ** IP: IDF line~9077 Object=CONTROLLER:MECHANICALVENTILATION, name=CONTROLLER MECHANICAL VENTILATION 1, Required Field=[Zone 1 Name] was blank.
   ** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
   ** Severe  ** IP: Possible incorrect IDD File
   **   ~~~   ** IDD Version:"IDD_Version 8.1.0.009"

How do I check to insure I have the correct IDD file? Thank you, Matt

MattStewart's avatar
565
MattStewart
asked 2014-12-30 00:24:53 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-07-12 18:13:14 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Hi Hason, I am having trouble with the forum. I am using Ideal Air and get the error. I've assigned thermostats using the Zone tab but do not see any reason to attach or modify equipment elsewhere.

MattStewart's avatar MattStewart (2014-12-30 09:39:56 -0500) edit
add a comment see more comments

2 Answers

4

The error message that you show is very rarely an indication that you are not using the correct IDD file, instead it usually indicates that you have a problem with a field in your input file. In this case, a filed that is supposed contain the name of a zone was left blank.

JasonGlazer's avatar
6.8k
JasonGlazer
answered 2014-12-30 06:27:48 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

See the answer to this question for causes of the controller:mechanical ventilation error.