Hello,

I'm studying a building with water to water heat pump plant system for cooling and heating.

I've designed in OS a cooling plant loop with cooling coil, pump variable speed and water-to-water heat pump: cooling and a condenser loop that I will be using with district cooling acting as ground geothermal condenser. For heating I will be using the same Setup with the necessary adjustments for the water-to-water heatpump:heating and distict heating.

I'm haveing trouble linking plant loop with correspondent condenser loop.

How can I link the water-to-water heatpump to the condenser loop?

Kastro1501's avatar
265
Kastro1501
asked 2016-12-15 08:19:51 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-12-15 13:31:31 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

This answer has essentially what you need to do, but with your HeatPump:WaterToWater instead of a water-cooled chiller.

They key part is that components connected to one loop can be found and dragged to a second loop from the 'My Model' tab in the right-hand pane.

ericringold's avatar
10.6k
ericringold
answered 2016-12-15 12:17:16 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks Eric, that solved the problema.