First time here? Check our help page!
2

Annual energy profile with extra data

I ran the example RefBldg Large Office model and found the below profile:

image description I have 2 questions 1. Is the extra data at the beginnings excluded from all annual reports? Which options control this profile under SimulationControl? 2. How can I remove this data from annual results .eso file and get a data in order of Jan to Dec.

rkbest's avatar
1.4k
rkbest
asked 2016-10-22 13:03:31 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-09-25 15:16:47 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

ResultsViewer might be choking on the "HVAC Sizing Simulations," try setting Do HVAC Sizing Simulation for Sizing Periods to No in SimulationControl and see if the problem goes away. If you want to use coincident plant sizing then may need to switch to a different plotting tool. Try with Run Simulation for Sizing Periods set to No as well. Also old translated example files don't usually have a name in the RunPeriod object and ResultsViewer seems to work better if you enter a name.

The annual tabular summary reports show the number of hours that were used in the annual summations at the top of the table report file. If that says 8760 hours, you can be sure the tabluar reports are for the one year. If you are using raw meter reports at the RunPeriod frequency, then you can verify their timeframe by checking that the values agree with the annual summary tables.

Archmage's avatar
7.2k
Archmage
answered 2016-10-24 09:18:04 -0500, updated 2016-10-24 10:40:41 -0500
edit flag offensive 0 remove flag delete link

Comments

The annual report says 8760 hrs, and once setting the SimulationControl as suggested, the ResultsViewer is not showing the earlier section. The simulation result is completed with some 14840 errors for reference building idf.

rkbest's avatar rkbest (2016-10-24 14:59:28 -0500) edit
add a comment see more comments