Can I set the natural ventilation depending of temperature and CO2 ppm?

I would like to activate the ventilation if temperatures reaches certain values and ppm reaches the value 1000, in order to maximize the internal air quality. in OPENSTUDIO

poppo92's avatar
875
poppo92
asked 2016-10-03 12:37:10 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-10-18 14:18:05 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Do you get the solution ? Can I ask you for help?

Done's avatar Done (2017-04-09 22:45:35 -0500) edit
add a comment see more comments

1 Answer

3

Which Ventilation method are you using ? The Airflow network or the simple Ventilation Design Flow rate etc.. ?

In any case I would say EMS is the answer to all those type of controls. You can just set your Ventilation schedule using Schedule: Constant.

Using EMS, set the temperature of the zone and the C02 concentration as sensors. The component to be actuated is the schedule value. Write your program to execute the control you want. There's quite a lot of literature on EMS in the Input/Output reference and the example files .

Jevin's avatar
197
Jevin
answered 2016-10-04 11:08:26 -0500, updated 2016-10-04 11:54:32 -0500
edit flag offensive 0 remove flag delete link

Comments

what is EMS?...

poppo92's avatar poppo92 (2016-10-04 11:31:20 -0500) edit

Energy Management System , though you will have to use EnergyPlus measures to insert the EMS code.

Jevin's avatar Jevin (2016-10-04 11:53:22 -0500) edit
ericringold's avatar ericringold (2016-10-04 11:59:00 -0500) edit

where can I find a EMS software for openstudio? is it difficult to learn it?

poppo92's avatar poppo92 (2016-10-05 04:54:25 -0500) edit
add a comment see more comments