Exhaust Heat Recovery

Hi all,

I am trying to model a system which has heat recovery coil designed at all exhaust air stream in E+. I can only see unitary system has the capability to add heat recovery coils at exhaust but my systems are mostly VAV distribution system. Any suggestion on how to model it?

Fish Lee's avatar
183
Fish Lee
asked 2016-09-12 22:34:52 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-09-13 06:41:50 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

I would take a look at the HeatExchanger:AirToAir objects in EnergyPlus (documentation HERE).

The HeatExchanger:AirToAir:SensibleAndLatent object is frequently used to approximate a sensible only run-around coil by setting the latent effectiveness to zero. You might check out the following posts for some additional insight on the use of this object...

Modeling run around loop in openstudio

Modeling Run-around loop Heat Recovery in EnergyPlus

Heat Exchanger and Outdoor Air Mixer

Lyle K's avatar
2.2k
Lyle K
answered 2016-09-13 15:28:25 -0500, updated 2016-09-13 15:35:30 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for your advise! I think I will explore the option of using EMS to modify the district heating loop input depending on the energy recovered from the exhaust air.