1

ASHRAE Loads in OpenStudio

Can Open Studio calculate ASHRAE loads?

clguen's avatar
153
clguen
asked 2016-09-12 15:56:28 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-09-13 06:43:33 -0500
edit flag offensive 0 remove flag close merge delete

Comments

1

Which loads? Outdoor air? Plug loads? Lighting loads? Please be more specific in your question.

TaylorRoberts's avatar TaylorRoberts (2016-09-12 16:14:03 -0500) edit
add a comment see more comments

1 Answer

5

If your question is, can OpenStudio apply ASHRAE 90.1-20xx assumptions to a model, then the answer is yes. Take a look at this repo. The thing you probably want is the baseline automation measure, which hasn't been published to the building component library yet, but should be very soon.

ljbrackney's avatar
3.8k
ljbrackney
answered 2016-09-13 09:32:11 -0500
edit flag offensive 0 remove flag delete link

Comments

Does Open Studio use the ASHRAE Heat Balance Method to calculate design heating and cooling space loads (like IES preforms)?

clguen's avatar clguen (2016-09-13 13:25:18 -0500) edit
1

OpenStudio doesn't perform any physics calculations itself; it uses EnergyPlus for that. And, yes, EnergyPlus uses the heat balance method.

__AmirRoth__'s avatar __AmirRoth__ (2016-09-13 13:42:02 -0500) edit

Yes, EnergyPlus is the engine and OpenStudio is the GUI. How do I view peak design heating and cooling space loads within the framework of OpenStudio?

clguen's avatar clguen (2016-09-13 13:44:34 -0500) edit

Look at the HVAC Sizing Summary table under EnergyPlus results.

__AmirRoth__'s avatar __AmirRoth__ (2016-09-13 14:08:41 -0500) edit

The OpenStudio standard report also has peak load summary plots.

ljbrackney's avatar ljbrackney (2016-09-13 14:23:28 -0500) edit
add a comment see more comments