Low Temperature Radiant : Electric

How can i model ZoneHVAC:LowTempratureRadiant:Electric system for the floor of the house in energy plus?. i already tried to design it by using the example provided with the software but when i run the simulation the result is not changing. i am just changing the schedules and the parameters related with this template.

khaled's avatar
33
khaled
asked 2016-08-23 06:05:20 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-08 18:34:27 -0500
edit flag offensive 0 remove flag close merge delete

Comments

You have not provided enough details to understand the issues that you facing.

JasonGlazer's avatar JasonGlazer (2016-09-12 09:17:05 -0500) edit
add a comment see more comments

1 Answer

2

This was also posted to the helpdesk with idf file. The problem was missing ZoneHVAC:EquipmentConnections and ZoneHVAC:EquipmentList objects.