ASHRAE 90.1-2007 App G PRM G3.1.2.4

As I have searched web and try to understand the 90.1 clause G3.1.2.4, the system needs to use night cycle and keep outdoor air flow rate to zero. I therefore just have a simple question, if above understanding is right, how re-circulation (no outdoor air) alone to meet the cooling/heating loads from zones during unoccupied hours? Do coils work as well during night cycle? Thank you very much in advance for any reply.

Sean King's avatar
31
Sean King
asked 2016-08-03 10:57:05 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-08-03 11:50:46 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

During unoccupied hours the outdoor air damper should close and then the unit should cycle on and off to meet the setback setpoint. To meet the setpoint, the heating and cooling coils should also turn on and off.

If you are using EnergyPlus/OpenStudio I can show you exactly how to do this, if you are using another program tell everyone and I am sure someone will know.

TaylorRoberts's avatar
2.9k
TaylorRoberts
answered 2016-08-03 15:41:17 -0500
edit flag offensive 0 remove flag delete link

Comments

Hi Taylor, Thank you very much for your reply. Yes, I am using EnergyPlus, could you please demonstrate me what to do? Thanks.

Sean King's avatar Sean King (2016-08-04 02:35:54 -0500) edit
add a comment see more comments