Insufficient Refrigerant Charge/Airflow

Is it possible for EnergyPlus to model an existing split or packaged heat pump system with low refrigerant charge and/or insufficient airflow? If so, how can this be accomplished? Are there any existing measures that attempt to address the modeling of these types of real-world system issues?

Thanks,

mjmurray's avatar
41
mjmurray
asked 2016-08-01 15:20:51 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-08-02 08:27:11 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

This Measure, which is not yet published on BCL, and which was written by Performance Systems Development contains logic to "undercharge" a DX system. As described in the measure.rb file, the primary source used to determine the COP degradation factors was this NIST report.

aparker's avatar
8.2k
aparker
answered 2016-08-01 20:10:30 -0500