Variable water flow condenser loop

Hi, does anyone know if it is possible to get variable flow pumping in your condenser water loop for heat rejection from a chiller? The example files provided with E+ that I have reviewed don't seem to allow this, only staged pumping. Cheers, Alex

ahespe's avatar
61
ahespe
asked 2016-07-26 02:15:35 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-07-26 08:03:37 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

That is correct, the chiller models all have constant flow requests on the condenser side. The condenser loop flow can vary If there is more than one chiller staging on and off, but not if there is only one chiller.