how to display total cooling/heating load

I tried load calculation for 5 zones but i can see zone sensible cooling and heating sensible sizing under zone overview tab of result. I am not sure whether is it total cooling/heating laod or just sensible cooling/heating. I m new to open studio/energyplus.

dipen609's avatar
145
dipen609
asked 2016-06-27 05:10:37 -0500
J Monteiro's avatar
1.2k
J Monteiro
updated 2016-06-27 09:10:46 -0500
edit flag offensive 0 remove flag close merge delete

Comments

1

"but i can see zone sensible cooling and heating sensible sizing under zone overview tab of result" I think the answer is in the question. If not, can you add a screenshot of the report you are looking at so we can answer accurately?

aparker's avatar aparker (2016-06-28 16:46:47 -0500) edit
1

I am having a similar issue. I would like to size cooling coils but where in the EnergyPlus or OpenStudio reports are the total coil capacities? Is there a report that a mechanical engineer could use for equipment selections? The EquipmentSummary coils capacities don't match up with the HVAC Sizing Summary design loads.