I have the following to remove all PIU reheat boxes and replace them with VAV reheat boxes. The variable airLoop is defined from do loop with mode.getAirLoopHVACs.each.

thermalZones = airLoop.thermalZones
thermalZones.each do |thermalZone|
    originalTerminal = thermalZone.airLoopHVACTerminal.get.to_AirTerminalSingleDuctParallelPIUReheat
    if not originalTerminal.empty?
        originalTerminal = originalTerminal.get
        reheatLoop = originalTerminal.reheatCoil.plantLoop.get
        originalTerminal.remove
        reheatCoil = OpenStudio::Model::CoilHeatingWater.new(model, model.alwaysOnDiscreteSchedule)
        reheatLoop.addDemandBranchForComponent(reheatCoil)
        newTerminal = OpenStudio::Model::AirTerminalSingleDuctVAVReheat.new(model,model.alwaysOnDiscreteSchedule(), reheatCoil)
        runner.registerInfo("The new terminal created is called '#{newTerminal.name}'.")
        thermalZone.addEquipment(newTerminal)
    end #end if not originalTerminal.empty?
end #thermalZones.each do |thermalZone|

It performs the desired task, but the OS:Connection objects aren't created and the terminal units don't appear in the loop graphics in the HVAC tab. I don't think addEquipment is the correct method to use but I'm not to grab the correct thermal zone inlet node in order to use the addToNode method. Anyone see what I'm missing here? Additionally, if there is something non-nonsensical or extraneous that I'm doing, please don't hesitate to let me know.

Adam Hilton's avatar
3.5k
Adam Hilton
asked 2016-06-20 10:39:21 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

Here are a couple snippets I've used to do something similar:

# get model and model objects
model = OpenStudio::Model::Model.load(osm_path).get
objs = model.getAirTerminalSingleDuctVAVNoReheats
air_loops = model.getAirLoopHVACs

# do stuff
air_loops.each do |al|

    zones = al.thermalZones

    zones.each do |z|

        al.removeBranchForZone(z)
        atu_new = OpenStudio::Model::AirTerminalSingleDuctUncontrolled.new(model, model.alwaysOnDiscreteSchedule)
        al.addBranchForZone(z, atu_new.to_StraightComponent)

    end

end

model.getThermalZones.each do |z|

    zone_eqpt = z.equipment #vector

    zone_eqpt.each do |eqpt|

        if eqpt.to_AirTerminalSingleDuctUncontrolled.is_initialized
            atu_old = eqpt.to_AirTerminalSingleDuctUncontrolled.get
            atu_old.remove
            atu_new = OpenStudio::Model::AirTerminalSingleDuctVAVNoReheat.new(model)

        end

    end

end
MatthewSteen's avatar
10.1k
MatthewSteen
answered 2016-06-20 12:19:00 -0500, updated 2016-06-20 13:05:12 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks Matt. I was trying to use the air loop addBranchForZone method but it doesn't appear to work with return plenums. I was thinking maybe I have to call it through the return plenum object (the addBranchForZone is listed under that object as well), but the thermal zone object doesn't seem to have a method that returns the AirLoopHVACReturnPlenum object.

Adam Hilton's avatar Adam Hilton (2016-06-20 12:29:40 -0500) edit

@adhilton are you trying to get the new zone branch to connect to the return plenum? I think you'll have to use the zone method setReturnPlenum after adding the new branch.

ericringold's avatar ericringold (2016-06-20 12:41:39 -0500) edit

The old ones also connect to a return plenum and that seems to be the problem. When I call airLoop.addBranchForZone nothing happens. If I call airLoop.removeBranchForZone first and then use addBranch it works fine and then I can manually add the return plenum back, but that doesn't seem like a very efficienct method.

Adam Hilton's avatar Adam Hilton (2016-06-20 12:45:47 -0500) edit

Oh, yeah if the zone is already on a loop, addBranchForZone will return false.

ericringold's avatar ericringold (2016-06-20 12:49:53 -0500) edit

Hmm, okay, thanks. Do you know how I can return the return plenum thermal zone using the thermal zone before I remove its' branch?

Adam Hilton's avatar Adam Hilton (2016-06-20 12:53:38 -0500) edit
add a comment see more comments