Can some one explain me if the properties that we insert on the fans, like the flow, are only to affect the output energy consumption? Or do they affect the flow on our air loop?

Because I wanted to control both the flow and the temperature of the air on my loop, but I am not being able to have 2 setpoints to control the Flow and the Temperature.

So, if I specifythe flow on the Fan will it affect my cooling and heating loads?

João Rodrigues's avatar
267
João Rodrigues
asked 2016-06-14 05:08:00 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-17 12:21:22 -0500
edit flag offensive 0 remove flag close merge delete

Comments

This is a generic question regarding energyplus rather than openstudio, so I retagged your question.

Julien Marrec's avatar Julien Marrec (2016-06-14 05:55:11 -0500) edit
add a comment see more comments

1 Answer

1

The Input/Output Reference Guide and his companion the Engineering Reference Guide are your friends.

If you take the Fan:ConstantVolume object for example, you see that the flow is actually a "Maximum Flow Rate". I think the name is pretty self explanatory: your fan just won't be able to go over this maximum flow rate.

The engineering reference guide has interesting sections, such as Air Loops - Determination of Air Mass Flow Rates

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2016-06-14 06:02:48 -0500, updated 2016-06-14 09:23:42 -0500
edit flag offensive 0 remove flag delete link