Warning - Calculated Relative Humidity out of range

I am constantly seeing this warning:

* Warning * Calculated Relative Humidity out of range (PsyRhFnTdbWPb) * ~~~ * Routine=CalcMultiSpeedDXCoil:lowspeedoutlet, Environment=RUN PERIOD 1, at Simulation time=04/12 13:00 - 13:10 * ~~~ * Dry-Bulb= 3.21 Humidity Ratio= 4.897E-003 Calculated Relative Humidity [%]= 101.01 * ~~~ * Relative Humidity being reset to 100.0%


Any thoughts on if this is something I can ignore?

nfonner's avatar
626
nfonner
asked 2014-12-05 12:43:43 -0500
Neal Kruis's avatar
4.7k
Neal Kruis
updated 2015-01-09 12:31:21 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

Hard to make a blanket comment without knowing more about what's happening in the model. A leaving dry-bulb temp of 3.2C (37.8F) is rather cold off a DX coil, so the airflow to capacity ratio for this coil may be too low.

MJWitte's avatar
9.7k
MJWitte
answered 2014-12-05 14:13:05 -0500
edit flag offensive 0 remove flag delete link

Comments

1

Looks like increasing the Constant Minimum Airflow Fraction above the minimum ventilation rate was part of the issue. The warning persists, but was much less "severe" at a DB to 9.48 C for that same model.