Pump setpoint manager

Hello, I'm modeling a plant in which a constant-speed circulation pump in the condenser loop must be on/off according to the zone air source heat pump on/off profile. Is there any set point-manager which is appropriate for that? Thank you so much.

Hamid's avatar
51
Hamid
asked 2016-05-28 08:02:24 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-05-29 09:28:38 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

If you set the 'Pump Control Type' field to 'Intermittent', the pump should only run when there is demand from the coils attached to the demand side of the loop. When the heat pump coils are scheduled off, there should be no demand and therefore no flow.