Gas coil not turning on-baseline system 3

I am modeling a project in EnergyPlus 8.0 that has a few system 3 baseline equipment with DX cooling and gas coil for heating. No matter how I have defined the settpoints for the gas heating coils, these coils do not turn on in the airloop. I have tried a zone average setpoint and schedules setpoints.

Has anyone had a similar problem? Is this a control issue or some sort of glitch?

Amir Rezaei's avatar
841
Amir Rezaei
asked 2014-12-05 08:31:59 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

1

Yes. I have found that you can build a system with Open Studio using: AirLoopHVAC Unitary Systems and gas heat does not turn on.

MattStewart's avatar
565
MattStewart
answered 2015-01-26 10:14:49 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

There is no known issue with this type of equipment. You have not said how you described this system (with an interface, or with HVACTemplate, or detailed unitary system, or ???). If you are working in native EnergyPlus, I would recommend that you use HVACTemplate:Zone:Unitary and HVACTemplate:System:Unitary and it should work just fine.