Openstudio doesn't calculate Design load with sizing factor [closed]

Hi I have a problem, Openstudio doesn't calculate Design load with sizing factor when I only use a thermostat for cooling. In my country we never use heating systems, so I don´t need to calculate the design load for heating. Thank you

dana94_08's avatar
211
dana94_08
asked 2016-05-27 09:07:31 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-03-07 22:03:58 -0500
edit flag offensive 0 remove flag reopen merge delete

Closed for the following reason "the question is answered, right answer was accepted" by dana94_08 2016-06-17 18:04:13 -0500

Comments

See if this post helps. It describes how to use ThermostatSetpointDualSetpoint when you want a cooling only system.

David Goldwasser's avatar David Goldwasser (2016-05-27 09:49:56 -0500) edit

What I did understand is that I have to put a heating schedule and it has to be with a lower temperature than my cooling schedule. So if I put a temperature of 12°C for the heating schedule there will be no mistake?

dana94_08's avatar dana94_08 (2016-05-27 10:35:25 -0500) edit

Yes, in addition to being lower than your cooling schedule, you may want it lower than any temperatures the building will see, so it doesn't show up as hours heating setpoint not met.

David Goldwasser's avatar David Goldwasser (2016-05-27 10:50:01 -0500) edit