Loop Design Temperature Difference

I can´t find within openstudio where to specify the loop design temperature difference for sizing plants, either for a chilled water or cooling tower loop. The autosizing reports that I am getting are assuming a default of 19.80 degrees Fahrenheit to autosize the pump flow rate. After exporting an idf file I am able to specify plant sizing parameters within the energyplus idf editor. Is this something that is not available within the openstudio application? Or is there a way to specify it within openstudio?

Carlos Vazquez's avatar
812
Carlos Vazquez
asked 2016-05-14 11:23:38 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The Plant:Loop and Sizing:Plant objects can be edited by clicking on the dashed line separating the Supply Equipment and Demand Equipment of the PlantLoop.

MatthewSteen's avatar
10.1k
MatthewSteen
answered 2016-05-15 08:26:58 -0500, updated 2016-05-15 08:28:18 -0500
edit flag offensive 0 remove flag delete link

Comments

I just verified it. That´s correct. Thank you your answer Matthew! I was not aware of that.

Carlos Vazquez's avatar Carlos Vazquez (2016-05-16 08:08:52 -0500) edit
1

problem solved then, please mark the answer as accepted by clicking on the check mark next to the post (to the left)

Julien Marrec's avatar Julien Marrec (2016-05-16 09:33:28 -0500) edit