Error running hvac system

hi, i've tried running my model with hvac system and come across this problem. the simulation run fine without hvac system. for test, i only attached vrf system to one thermal zone only.

tq.

Initializing HVAC **FATAL:Errors getting Zone Control input data. Preceding condition(s) cause termination. EnergyPlus Run Time=00hr 00min 8.00sec

grantt006's avatar
13
grantt006
asked 2016-05-12 23:53:25 -0600
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-06 08:36:30 -0600
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Sounds like you are missing a thermostat for this zone. Add htg and clg schedules on the Thermal Zones tab.

aparker's avatar
8.2k
aparker
answered 2016-05-14 07:42:19 -0600
edit flag offensive 0 remove flag delete link

Comments

Thank you, that was helpful. i only put clg thrmostat and left htg thermostat column empty.