Secondary chiller in plant loop in 5ZoneVAV Chilledwaterstorage idf

In the EnergyPlus Example files for Chilled Water Storage-Mixed vs Stratified(5ZoneVAV-ChilledWaterStorage-Mixed.idf & 5ZoneVAV-ChilledWaterStorage-Stratified.idf), the Secondary chiller is present in the Mixed storage idf while only Primary in stratified idf file. What is the logic or rule to configure the plant loops and when we should consider using two chillers vs only one with TES implemented?

rkbest's avatar
1.4k
rkbest
asked 2016-05-11 10:31:21 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-10-21 12:33:15 -0500
edit flag offensive 0 remove flag close merge delete

Comments

1

Unless the author of these files comes by, I'll go on a limb and say that there's no logic or rule, they just decided to put another one... It might not even have been the same person that did the two examples.

Julien Marrec's avatar Julien Marrec (2016-05-12 10:42:25 -0500) edit
add a comment see more comments