Eplus unusual warning

I was trying to simulate in Eplus a double skin façade with four vertical thermal zones (subzones) when I got this Warning: "Inside surface heat balance did not converge with Max Temp Difference [C] =2.026E-003 vs Max Allowed Temp Diff [C] =2.000E-003"

What's the correlation with Heat balance algorithm? Can anyone help me?

Conduction transfer

Thank You

luis melo's avatar
225
luis melo
asked 2016-05-06 10:21:00 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2016-05-09 03:59:19 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

In my view, you can try to reset the maximum surface convection heat transfer coefficient value to the default value 1000. I'm not sure whether this method can solve your problem, just a suggestion.

gaofeng's avatar
225
gaofeng
answered 2016-05-07 06:30:14 -0500
edit flag offensive 0 remove flag delete link

Comments

It was my first option, and doesn't work.

Thank you!!

luis melo's avatar luis melo (2016-05-09 03:53:18 -0500) edit

The problem is solved. I changed the numbers of timesteps from 6 to 12. Lower number of time steps leds to higher delta T between the timesteps (higher than Temperature Convergence Tolerance).

luis melo's avatar luis melo (2016-05-18 04:02:42 -0500) edit