Ideal Loads and Economizer set up [closed]

I need to run simulations in which the cooling and heating loads are supplied via Ideal Loads. I have opened another question here which I have followed, but working on the model have brought other questions to my mind. I have used the "ideal loads" option to model the air conditioning system, setting the ACH as indicated to me in the previous question, the simulation ran and I compared these variables:

-Zone Ideal Loads Zone Sensible Cooling Rate

-Zone Ideal Loads Supply Air Sensible Cooling Rate

which are exactly equal. As far as I know, there should be a difference between the two variables if the system is supplying unconditioned outdoor air whenever the outdoor air temperature is suitable in order to save energy.

I am then asking you, how can I understand if the OA is supplied (using OpenStudio) and what option/parameters shall I check in order to model the system correctly?

Thanks

FSilenzi's avatar
609
FSilenzi
asked 2016-04-27 03:59:45 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-10-18 07:20:27 -0500
edit flag offensive 0 remove flag reopen merge delete

Closed for the following reason "question is not relevant or outdated" by FSilenzi 2016-06-10 02:42:13 -0500

Comments

add a comment see more comments

1 Answer

2

Like for the ...Supply Air... and the ...Zone... output variables there are also a set of ...Outdoor Air... output variables for the ideal air loads system. You can use that to check the energy/rates for outdoor air.

OS leaves all the parameters in the IdealLoadsAirSystem object to defaults, and I don't believe you can change anything in the GUI, so you'll have to write a measure. The default for the outdoor air parameter is to not have any outdoor air which would explain the lack of difference you're seeing.

Adam Hilton's avatar
3.5k
Adam Hilton
answered 2016-04-27 10:36:35 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks @adhilton If such a measure would exist I shall find it on the BCL right? Or is there another repository/library which I can check?

FSilenzi's avatar FSilenzi (2016-04-28 01:42:07 -0500) edit

I managed to input the correct objects for Ideal Loads in E+ idf editor, and the simulation seems to run seamlessly. I have temperature match as well as hourly air changes satisfy the requirements. What still confuses me is how can I check if the enconomizer is working, because I have Zone Ideal Loads Economizer Active Time as output, as well as Zone Ideal Loads Supply Air Sensible Heating Rate (a) and Zone Ideal Loads Zone Sensible Heating Rate (b). I have a different from b even if the economizer has 0 hours of functioning. Why this could happen?

FSilenzi's avatar FSilenzi (2016-05-02 03:07:43 -0500) edit

You could have a heating limit set or a specified minimum of outdoor air being brought in. Other than that, not really sure.

Adam Hilton's avatar Adam Hilton (2016-05-02 08:40:51 -0500) edit

ZoneHVACIdealLoadAirSystem has "heating limit" set to "no limit". The only limits I have set are for cooling because I could not turn on the economizer without setting "cooling limit" as "limit flow rate" and the "maximum cooling rate flow rate" set to autosize.

FSilenzi's avatar FSilenzi (2016-05-02 09:45:31 -0500) edit