Seperate zones in one thermal zone

In my case study, I have three refectories (refectory 1,2,3) that they are adjacent to each other with voids among them.

image description

There is two options that I would like to know which one could be better?

  1. Designing these three refectories in one zone with one thermal zone.

  2. Designing these three refectories in separate zones but Considering in one thermal zone.

Thanks in advance for any answers!

4Designer's avatar
738
4Designer
asked 2016-04-25 15:02:20 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2016-04-25 15:27:51 -0500
edit flag offensive 0 remove flag close merge delete

Comments

1

How are they being conditioned and controlled? That will impact if they have to be modeled as separate zones or can be modeled as one zone. I assume your option 2. is as separate zones, but with zone mixing between 1 to 2, and 2 to 3.

A third option if the temperatures are similar and airflow across zones is minimal is to model them as separate zones without any air mixing between the zones.

David Goldwasser's avatar David Goldwasser (2016-04-25 15:38:30 -0500) edit

@David Goldwasser , Thank you David.

4Designer's avatar 4Designer (2016-04-26 12:52:03 -0500) edit

Hi, may i ask if you have modelled those voids as opaque elements or transparent one, in order to follow these rules as explained in this link? http://energyplus.helpserve.com/Knowl...

Futhermore: is the glass aperture in refectory 2 a geometry that will cause a severe error because is a no convex zone?

Thanks in advance

lukanuts's avatar lukanuts (2018-08-09 04:15:29 -0500) edit
add a comment see more comments

1 Answer

1

Maybe the ISO 13790 can help you to decide.

"In particular you have not to dived a space in more thermal zone if:

  1. Set-point temperatures for heatingcooling of the spaces differ by no more than 4 K;

  2. The spaces is serviced by the same heating systeme (if any) and the same cooling system (if any);

  3. At least 80% of the floor area are serviced by the same ventilation system;

  4. The ammount of ventilation (in cubic metre per square metre of floor area per second) differs by not more than a factor of 4 within 80% of the floor area."