Dehumidification control on packaged unitary in Energy Plus

I am attempting to use a dedicated outdoor air unit (Packaged Unitary HVAC) in energyplus 8.0 so that it does sub-cooling of outdoor air in response to zone humidity levels rising above a humidity threshold. Currently, the "Dehumidification Control Type" is set to "CoolReheat", there is a humidistat in the control zone, and a maximum humidity schedule has been defined at 50%.

Per the I/O manual, I created a TwoStagewithHumidityControl coil and was able to associate this with the desuperheater. However, I am not able to see the option to connect the TwoStageWithHumidityControl coil on the drop-down list of cooling coil choices for the system. When I enter the coil name manually, multiple errors arise. Among them, "Illegal Cooling Coil Object Type=Coil...HumidityControl"

Is this the right approach to basic humidity control? Anyone know what's going on here?

E Boxer's avatar
111
E Boxer
asked 2014-12-01 16:13:50 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-07-11 13:07:32 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

5

This depends on your equipment type. Coil:Cooling:DX:TwoStageWithHumidityControlMode models a system which has two operating modes, normal and subcool reheat (altered SHR). This coil is supported by AirloopHVAC:UnitarySystem, AirLoopHVAC:UnitaryHeatCool:VAVChangeoverBypass and CoilSystem:Cooling:DX. If you are modeling a standard single-speed DX coil which simply runs longer to overcool and dehumidify, then you can use Coil:Cooling:DX:SingleSpeed with AirLoopHVAC:UnitaryHeatCool.

MJWitte's avatar
9.7k
MJWitte
answered 2014-12-03 12:48:21 -0500
edit flag offensive 0 remove flag delete link

Comments

Michael,

Thank you, your comment is greatly appreciated and got me on the right track. The first problem was in using e+ 8.0. Energyplus 8.1 and 8.2 have been updated to allow the use of TwoStageWithHumidityControl coils on the system type AirLoopHVAC:UnitarySystem. It is still not available with the UnitaryHeatCool system type.

E Boxer's avatar E Boxer (2014-12-03 14:44:01 -0500) edit
add a comment see more comments
1

According to the I/O manual, the TwoStageWithHumidityControl coil type is not allowed on systems of type UnitaryHeatCool. The best option would be to simulate with another system type. In energyplus 8.1 and onwards, the TwoStageWithHumidityControl coil type is allowed with system type "AirLoopHVAC:UnitarySystem", which also has other extended capabilities beyond those found in the "UnitaryHeatCool" system type.