1

Sizing of DX Cooling Coil and performance of ITEquipment

I am trying to study the effect of mass flow rate and deltaT (input-output temperature difference) on the performance of IT equipment and data centers using two schemes, a steady-state one built into E+ and a transient scheme for servers developed experimentally. The goal is to characterize the difference in CRAC performance and mechanical PUE when comparing the two schemes. The cooling system used is DX Cooling (DXCoolingCoil:SingleSpeed).

However, what I have found is that there is no difference in facility total power, facility building power (quotient of which gives PUE), the CRAC power, DX cooling coil power and system flow rate when I implement the two schemes.

1) My understanding is that a higher deltaT and hence higher exit temperature would result in greater power savings in terms of the HVAC system but E+ does not report any difference in any of the above parameters.

2) Hard Sizing the DX coil to produce changes in mass flow rate and inlet air temperatures does not seem to work. Either errors are reported that there is a mismatch in sizing of various components or that zone temperatures are too high. Auto-sizing the coil (rated capacity, rated flow rate and SHR) seems to produce optimum results in terms of cooling system power consumed and PUE; however, that technique does not work with my transient scheme where E+ reports the supply side air flow rate to be around 2.8 kg/s and the ITE mass flow rate to be around 22kg/s, which does not make physical sense, even taking re-circulation into account.

Has anyone seen such a situation or can shed some light as to how to go about this and characterize the performance. Doing it experimentally is one thing but simulation should support those results. I would highly appreciate any insight into this situation.

Rehan Khalid's avatar
197
Rehan Khalid
asked 2016-03-13 16:17:05 -0500
Jason DeGraw's avatar
2.2k
Jason DeGraw
updated 2016-03-15 09:25:38 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Please explain what the "transient" scheme is. The comment about auto-sizing leads me to believe that the sizing for the transient case is not sizing on the peak ITE load - possible schedule problem?

MJWitte's avatar MJWitte (2016-03-18 13:32:00 -0500) edit

The transient scheme pertains to how the exit air temperature is calculated. Currently EP calculates the exit air temperature using a steady-state equation: T_a_ex = T_a_in + (Q/m_dot*c_p_air)

We are calculating the exit air temperature taking into account the server thermal mass (capacitance and time constant, for which various empirical correlations have been developed), server temperature and the exit temperature at previous time steps.

We believe that the time constant should produce a lag in exit temperature and hence would affect the cooling load and demand. However, that is not to be.

Rehan Khalid's avatar Rehan Khalid (2016-03-23 09:54:01 -0500) edit
add a comment see more comments

1 Answer

1

There are 2 methods for controlling HVAC systems, specifically the coils. One is load based, the other set point based. If you are trying to simulate a change in supply air temperature with a corresponding change in supply air flow rate, the set point based method may better represent your intent.

Regardless of the method used, coil performance is a function of the inlet air condition, which is represented through performance curves. As the coil air inlet air condition (wet-bulb temperature) increases, the cooling capacity increases while the energy use decreases (a result of higher refrigerant suction temperature/pressure). You should see this result in the hourly simulation output.

However, there is a well known mantra that the load is the load is the load. If you are seeing similar results, I suspect that the zone temperatures are similar, which means you are meeting the same load (and also should see similar coil entering air conditions). If this load is met using a higher supply air temperature, at the expense of added fan power and fan heat, the question is then what optimal combination works best.

Without seeing very specific system sizing results it is very hard to provide more specific guidance.

rraustad's avatar
13.8k
rraustad
answered 2016-04-05 18:39:21 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you Sir. That is good insight into the problem. I will explore further from here.

Rehan Khalid's avatar Rehan Khalid (2016-04-07 14:57:26 -0500) edit
add a comment see more comments