Temperature of Nodes around heat exchanger is not reasonable

I used OpenStudio to model a high school buildings in the cold area. There are heat exchangers in its AHUs for energy recovery between outside air and exhaust air. After checking the modeling output in ResultsViewer, the temperature of two nodes around heat exchanger is not reasonable for me. When the OA Temperature (Node 237) is low and exhaust air temperature (Node 213) is high, the OA temperature after heat exchanger (Node 212) is higher than exhaust air temperature after heat exchanger (Node 209), which is not reasonable for me. The detailed air loop and temperature variation are showed as followings. Does anyone know why it would happen? Thanks!

image description image description image description

lyw0211's avatar
429
lyw0211
asked 2016-03-02 10:41:29 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-04 09:09:03 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

This should be possible when the heat exchanger is counterflow.

Ivan Korolija's avatar
911
Ivan Korolija
answered 2016-03-03 09:02:38 -0500
edit flag offensive 0 remove flag delete link

Comments

@Ivan Korolija, Thank you for your answer. That will be helpful!