Using Coil:Cooling:WaterToAirHeatPump:EquationFit

I want to use Coil:Cooling:WaterToAirHeatPump:EquationFit (doc) to model a water-cooled DX unit.

Can I use this coil directly on the supply side of an AirLoopHVAC or do I necesarilly need to package it inside a AirLoopHVAC:UnitarySystem object?

Julien Marrec's avatar
29.7k
Julien Marrec
asked 2016-03-02 10:11:10 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

It needs to go inside an AirLoopHVAC:UnitarySystem or a ZoneHVAC:WaterToAirHeatPump.

Archmage's avatar
7.2k
Archmage
answered 2016-03-02 18:35:44 -0500
edit flag offensive 0 remove flag delete link

Comments

I looked at all example files and tried it purely on an AirLoopHVAC and came to the same conclusion. But I couldn't find anywhere in the documentation where that is stated. Did I miss it or is the documentation lacking?

Julien Marrec's avatar Julien Marrec (2016-03-03 02:35:41 -0500) edit